    A brief summary of our experience with EFOY methanol fuel cells was
    that in four separate deployments the system ended up running from
    1-6 weeks before shutting down with a blinking fault indicator.<br>
    It generally took 1-4 months to return to the site to assess the
    issues-back pressure on outlet tube, dehydration of fuel core,
    unknown (just pushed button to resume) , etc.  <br>
    <br>
    Regarding the plastic fuel cartridges.  We had one develop a small
    split at a seam in the plastic-presumably due to cold and/or
    shipping.  This resulted in a puddle of methanol, which in field
    conditions is not easy to distinguish from water puddles.  Methanol
    has a clear flame and its quite hard to see if the puddle is
    alight.  So there is a threat of of burning yourself or worse, the
    plastic tank melting, leaking, whoosh... <br>
    <br>
    Roy Stehle of SRI has successfully run one for 3 winters on the
    north slope, powering a VSAT. Which is very impressive.<br>
    <br>
    For us, the prospect of routinely visiting to fill up methanol, was
    less economical than larger batteries that can recharge without a
    visit.<br>
    We also have very high cost to visit.  The economics are much more
    favorable if the site is a few hours drive that you can schedule in
    the coming week or so.<br>
    And you have data coming in telling you what its doing.   So it
    certain circumstances they might work well.  <br>
    We'll probably try ours again in Southeast AK where its dim solar
    always and there are people around.<br>
    <br>
    Integrated packages for methanol fuel cells and propane fuel cells
    available at:<br>
    <span style="color: #333333;" color="#333333" size="2">
      <div style="text-align: left; color: #4c0171; font-family:
        Verdana, Geneva, Arial, Helvetica, sans-serif;" align="left"><strong><b><span
              style="color: #333333;" color="#333333" size="2">
              <div style="text-align: left; color: #000000; font-family:
                Verdana, Geneva, Arial, Helvetica, sans-serif;"
                align="left">Sirius Integrator</div>
            </span></b></strong></div>
    </span><span><strong><b><span style="color: #333333;"
            color="#333333" size="2">
            <div style="text-align: left; color: #000000;" align="left"><a
                style="color: rgb(0, 102, 255); text-decoration:
                underline;" shape="rect"
href="http://r20.rs6.net/tn.jsp?f=001ROlgzaXon3fijUnDQqcjUVj0V6ZL4fGAQg8iqNTwdX1qFVcF58Giq-N0pLrwaT-P1Z2KR7MnRA2mSoWCagyddHFPQgvuysZxp0p1MJj2hgxh8m9c6jye2SJYPOZ27l9JxVHrGCTOavxGG6q9gv33loX6m-D5onlIvC3eDVdTUw_ErVAT3N7e4v40AZsspYYi7PkXBkwgFuVe8JG58Hahn2UGsIMw_tQlNpIp-7-5GaP94DueX6JL3rOYVcxxhZi2CYYlCxIB4S_a1vt_2HX7JhRIvOMWrSA5Aoy-v4fJAq0ciD5rfB2wyZ4nsNlsm7b5dT_oKHHRBGifXzDq-QQm-Q==&c=ryW-j55Pie0tXYfCnXbFieca7qibtuko5k_L775MZ6AgCh9SaYjtNw==&ch=xqztRwPdzMjsdD0fYQiCdGTWE8jgUoTfRkdi3xaK4juNW3yQNPqO4w=="
                target="_blank">www.siriusintegrator.com</a></div>
            <div style="text-align: left; color: #000000;" align="left"><a class="moz-txt-link-abbreviated" href="mailto:John@siriusintegrator.com">John@siriusintegrator.com</a></div>
            <div style="text-align: left; color: #000000;" align="left">855-747-4874</div>
          </span></b></strong></span><br>
    <br>
    <div class="moz-cite-prefix">On 1/7/2015 2:20 PM, John R Evans
      wrote:<br>
    </div>
    <blockquote cite="mid:5D8265ED-2DC1-4FCD-AC04-D49FE0068310@usgs.gov"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      Hi All,<br>
      <div apple-content-edited="true">
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; "><br>
        </div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; ">Agreed —
          excellent discussion.</div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; "><br>
          We (Dave Croker and I) will know more soon, but I certainly
          agree that more panel and battery and better controllers are a
          preferable solution in nearly all locations.<br>
          <br>
          There are a few sites where cost (versus a load of 28
          batteries via helicopter) or always-dark conditions (bottom of
          redwood-lined V-canyon in the PNW) might still argue for a few
          fuel cell in spite of the initial cost.  Fuel is just
          methanol.</div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; "><br>
        </div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; ">Suspect
          thermoelectric has too much fire potential for many locations
          (used them in Idaho in the way-back-when and they scared the
          heck out of me so near dry pines).</div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; "><br>
        </div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; ">Anyone have
          specific experience with reliability of the SFC cells?  Bob?</div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; "><br>
        </div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; ">They are
          mil-spec for the German military (likely though, but even
          costlier), so might be better for those rare candidate sites
          if we know nothing else; might be worth one test anyway.
           Their contact info changed, by the way:</div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; "><br>
        </div>
      </div>
      <blockquote style="margin: 0 0 0 40px; border: none; padding:
        0px;">
        <div apple-content-edited="true">
          <div style="orphans: 2; text-align: -webkit-auto; text-indent:
            0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
            space; -webkit-line-break: after-white-space; ">SFC Energy
            AG<br>
            Christian Böhm<br>
            VP Defense and Security Business<br>
            Eugen-Saenger-Ring 7<br>
            85649 Brunnthal/München<br>
            Germany<br>
            +49 (89) 673.592.364<br>
            +49 (160) 90.52.74.72<span class="Apple-tab-span"
              style="white-space:pre"> </span><Cell<br>
            +49 (89) 673.592.169<span class="Apple-tab-span"
              style="white-space:pre"> </span><FAX<br>
            <a moz-do-not-send="true"
              href="mailto:Christian.Boehm@sfc.com">Christian.Boehm@sfc.com</a><br>
            <a class="moz-txt-link-abbreviated" href="http://www.sfc.com">www.sfc.com</a><br>
            <a class="moz-txt-link-abbreviated" href="http://www.efoy-pro.com/page/efoy-proenergybox">www.efoy-pro.com/page/efoy-proenergybox</a><br>
             <br>
            Björn Ledergerber<span class="Apple-tab-span"
              style="white-space:pre"> </span>(U.S. Rep.)<br>
            <a class="moz-txt-link-abbreviated" href="mailto:Bjoern.Ledergerber@sfc.com">Bjoern.Ledergerber@sfc.com</a></div>
        </div>
      </blockquote>
      <div apple-content-edited="true">
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; "><br>
        </div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; ">Dave and I
          will let you know more when we know it, including at least
          rough costs and fuel-use rates and costs.  We will assume up
          to 0.6 W at 12 V (500 mA) if no one objects.</div>
        <div style="orphans: 2; text-align: -webkit-auto; text-indent:
          0px; widows: 2; word-wrap: break-word; -webkit-nbsp-mode:
          space; -webkit-line-break: after-white-space; "><br>
          Cheers,<br>
          John<br>
          <br>
          John R. Evans<br>
          <br>
          -------------------------<br>
          <br>
          831-460-7593 direct<br>
          408-209-6219 mobile<br>
          <a moz-do-not-send="true" href="mailto:jrevans@usgs.gov">jrevans@usgs.gov</a><br>
          <br>
          -------------------------<br>
          <br>
          Normally at (mail or shipping):<br>
          U.S. Geological Survey<br>
          400 Natural Bridges Dr<br>
          Santa Cruz  CA  95060<br>
          <br>
          -------------------------<br>
          <br>
          Intermittently at:<br>
          <br>
          Mail ONLY<br>
          USGS/ASL<br>
          P.O. Box 82010<br>
          Albuquerque  NM  87198-2010<br>
          <br>
          Shipping ONLY<br>
          USGS/ASL<br>
          Target Rd 10002 Isleta SE<br>
          Kirtland AFB  NM  87117<br>
          <br>
          -------------------------<br>
          <br>
          We have found the ground.<br>
          <br>
          <span class="Apple-tab-span" style="white-space: pre; "> </span>--
          JPL, Curiosity control room<br>
          <br>
          -------------------------<br>
          <br>
          <br>
          <br>
          <br>
          <br>
          --------------------------------------------------<br>
          <br>
          <br>
          <br>
        </div>
      </div>
      <br>
      <div>
        <div>On 2015-Jan-07, at 10:40 , <a moz-do-not-send="true"
            href="mailto:anss-netops-request@geohazards.usgs.gov">anss-netops-request@geohazards.usgs.gov</a>
          wrote:</div>
        <br class="Apple-interchange-newline">
        <blockquote type="cite">Send ANSS-netops mailing list
          submissions to<br>
          <span class="Apple-tab-span" style="white-space:pre"> </span><a
            moz-do-not-send="true"
            href="mailto:anss-netops@geohazards.usgs.gov">anss-netops@geohazards.usgs.gov</a><br>
          <br>
          To subscribe or unsubscribe via the World Wide Web, visit<br>
          <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
          or, via email, send a message with subject or body 'help' to<br>
          <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-abbreviated" href="mailto:anss-netops-request@geohazards.usgs.gov">anss-netops-request@geohazards.usgs.gov</a><br>
          <br>
          You can reach the person managing the list at<br>
          <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-abbreviated" href="mailto:anss-netops-owner@geohazards.usgs.gov">anss-netops-owner@geohazards.usgs.gov</a><br>
          <br>
          When replying, please edit your Subject line so it is more
          specific<br>
          than "Re: Contents of ANSS-netops digest..."<br>
          <br>
          <br>
          Today's Topics:<br>
          <br>
            1. Re: solar power problems (Philip Crotwell)<br>
            2. Re: ANSS-netops Digest, Vol 59, Issue 6 (Greg Steiner)<br>
          <br>
          <br>
----------------------------------------------------------------------<br>
          <br>
          Message: 1<br>
          Date: Wed, 7 Jan 2015 12:32:48 -0500<br>
          From: Philip Crotwell <a class="moz-txt-link-rfc2396E" href="mailto:crotwell@seis.sc.edu"><crotwell@seis.sc.edu></a><br>
          To: Patrick Bastien <a class="moz-txt-link-rfc2396E" href="mailto:bastienp@ldeo.columbia.edu"><bastienp@ldeo.columbia.edu></a><br>
          Cc: <a class="moz-txt-link-rfc2396E" href="mailto:anss-netops@geohazards.usgs.gov">"anss-netops@geohazards.usgs.gov"</a><br>
          <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-rfc2396E" href="mailto:anss-netops@geohazards.usgs.gov"><anss-netops@geohazards.usgs.gov></a><br>
          Subject: Re: [ANSS-netops] solar power problems<br>
          Message-ID:<br>
          <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-rfc2396E" href="mailto:CAGFrVcWYkYVwpZeZeamvSc_+vL91zN0gW3qoqGZntLXf+kgrWQ@mail.gmail.com"><CAGFrVcWYkYVwpZeZeamvSc_+vL91zN0gW3qoqGZntLXf+kgrWQ@mail.gmail.com></a><br>
          Content-Type: text/plain; charset="UTF-8"<br>
          <br>
          We use the same batteries. But get the PVX-1040HT if you can
          as they<br>
          have a (H)andle. Very useful!  :)<br>
          <br>
          Philip<br>
          <br>
          On Wed, Jan 7, 2015 at 12:18 PM, Patrick Bastien<br>
          <a class="moz-txt-link-rfc2396E" href="mailto:bastienp@ldeo.columbia.edu"><bastienp@ldeo.columbia.edu></a> wrote:<br>
          <blockquote type="cite">The Concorde Sun Extender PVX-1040T
            has a nominal capacity of 104AH, so<br>
            312AH for the northern TA stations and 208AH for the
            southern TA stations.<br>
            <br>
            Beginning late last summer, the LCSN has begun to switch
            from older<br>
            PWM-style charge controllers to MPPT charge controllers.
            Although it is too<br>
            soon to say something definite, this is seeming to have a
            larger effect on<br>
            station up-time than just adding more panels or batteries.
            Something I am<br>
            doing that might be considered non-standard is wiring each
            solar panel<br>
            individually to its own small MPPT change controller. This
            allows each solar<br>
            panel to generate the maximum amount of power regardless of
            the lighting<br>
            condition of the other solar panels. The several MPPT charge
            controllers<br>
            then feed a common battery bank. I then regulate the voltage
            powering the<br>
            sensor by using a small low-noise DCDC converter imbedded
            inside a cable.<br>
            The MPPT benefits might be magnified for the LCSN because of
            the location of<br>
            many of our solar powered stations are in forests or
            forest-adjacent.<br>
            <br>
            <br>
            Patrick Bastien<br>
            LDEO-LCSN<br>
            <br>
            <br>
            On 1/7/2015 11:06 AM, Meremonte, Mark wrote:<br>
            <br>
            Bob,   May I ask the AH size of AGM batteries for an average
            TA station?<br>
            Thank you, Mark<br>
            <br>
            On Wed, Jan 7, 2015 at 8:29 AM, Robert Busby
            <a class="moz-txt-link-rfc2396E" href="mailto:busby@iris.edu"><busby@iris.edu></a> wrote:<br>
            <blockquote type="cite"><br>
              Hi Mitch et al.<br>
              This is a good discussion of Power for seismic stations,
              thanks.<br>
              <br>
              In the Transportable Array deployment, all 1717 stations
              operate(d) off<br>
              solar power for at east two years.  The average current
              draw for a station<br>
              is 0.5Amps on a 12V system, but can vary from 0.4 to 0.6A
              depending on the<br>
              telemetry system. High current telemetry systems such as
              VSAT are powered<br>
              separately.  We avoided AC power because of the proximity
              of noise due to<br>
              pumps, motors, etc.<br>
              <br>
              In general we use (2) 90W PV panels and (2) AGM Lead Acid
              batteries for<br>
              stations south of the Kentucky/Tennessee line (row U in TA
              station codes)<br>
              and (3) 90W PV panels and (3) AGM Lead Acid batteris north
              of there. Shady<br>
              or snowy sites occasionally got more panels and batteries.
               For permanent<br>
              stations I'd go with the (3) PV and 3 or 4 batteries.  We
              prefer good<br>
              quality batteries designed for solar applications, such as
              the Concorde Sun<br>
              Extender PVX-1040T.  We use PWM regulators with Low
              voltage disconnect at<br>
              10.8V.   A few more sophisticated options are discussed
              below.<br>
              <br>
              I would concur with the notion that the most effective way
              to improve a<br>
              marginal station power situation is to add 1 or 2
              batteries, and often this<br>
              can be done without much infrastructure alteration. And
              the next  option is<br>
              to add a panel.  There is little concern about over
              driving the charge<br>
              controller with too much current from too many panels.  In
              Alaska, the "more<br>
              batteries" approach is taken to extremes in which stations
              have 24 batteries<br>
              to float through the winter. I would also concur that, to
              date, neither wind<br>
              nor fuel cells have proved reliable enough to warrant
              their use, especially<br>
              in permanent stations of the Lower48.<br>
              <br>
              More complexity described below:<br>
              Our system has, in addition to the main battery bank, a
              small reserve<br>
              battery.  When the system switches to the reserve, certain
              loads such as the<br>
              telemetry radio and local data storage are duty cycled at
              four hour<br>
              intervals.  This reduces the power of the station to about
              3W, yet still<br>
              provides complete telemetry (though with episodic latency)
              and complete<br>
              local storage.  For us, this reserve power serves to
              identify the source of<br>
              the outage is clearly power as opposed to a host of other
              possibilities.  In<br>
              the original design this reserve battery was Alkaline
              Lattern 30AH batteries<br>
              [(3) x 6Volts] (a primary battery, disposed of after use).
               More recently,<br>
              We have also used 100-300AH rechargeable batteries that
              are then connected<br>
              to the main batteries using a battery isolator
              circuit-which connects the<br>
              reserve batteries to the charger only when the main
              battery has recharged to<br>
              13.2V.  We add a 10A current limit to the battery
              interconnection.  The<br>
              reserve power load shedding  can be thought of as doubling
              the capacity of<br>
              the reserve batteries, reducing the cost of overall power
              system for this<br>
              reserve capability.  Without that sophisitication of load
              shedding, adding<br>
              more batteries is effective but there is a cost in terms
              of station uptime.<br>
              When a very large, undifferentiated battery bank is
              depleted, it will take a<br>
              longer time for the batteries to reach the reconnect
              voltage.  In this time,<br>
              the station itself could be operating on the minimal power
              produced. We keep<br>
              the main battery bank fairly modest so it recovers voltage
              quickly, and<br>
              defer recharging the reserve pack until there is ample
              power-sometimes<br>
              weeks, or in Alaska, months later.  Its meant to get you
              through an<br>
              ocasional bad spell.  One issue in this reserve battery
              switching is the dc<br>
              currents can introduce magnetic pulses seen on the
              seismometer-particularly<br>
              Trilliums within a few meters of the switches.<br>
              <br>
              If you are plannning a Net-ops meeting in the future, I'd
              be happly to<br>
              elaborate on the power system for Alaska, which uses a
              Genasun MPPT charge<br>
              controller and LiFePO4 (Lithium Ion) batteries and the
              same duty cycle<br>
              loads, reserve battery concepts.  These significantly
              reduce the weight of a<br>
              1440AH system to 420 lbs and do not require derating the
              capacity for cold<br>
              temperatures.  They are very expensive, but not as much as
              a helicopter<br>
              trip.<br>
              <br>
              Bob Busby<br>
              TA Manager<br>
              <br>
              On 1/6/2015 7:36 AM, Kyle Persefield wrote:<br>
              <blockquote type="cite"><br>
                Mitch,<br>
                <br>
                My 2 cents worth<br>
                <br>
                Because of cost, we have found throwing on more solar
                panels to be the<br>
                cheapest and least maintenance intensive solution.  Fuel
                cells and<br>
                thermoelectric generators are expensive and then there
                is the recurring<br>
                cost for fuel, getting fuel to the site, then monitoring
                of the fuel<br>
                supply level to consider, and the added required
                maintenance.  We have<br>
                not<br>
                found a solution to use these devices as demand requires
                their use.  Or<br>
                turning them on and off as needed.  So long as there is
                fuel they are on.<br>
                <br>
                We have been very disappointed with wind turbines.  The
                smaller ones,<br>
                which are designed for the consumer market, the bearings
                always fail.<br>
                Expect no more than 2 or3 years out of these "cheap"
                units.  Then of<br>
                course there is the need for wind.  No wind for extended
                periods is just<br>
                as bad as your overcast scenario.<br>
                <br>
                Kyle<br>
                <br>
                -----Original Message-----<br>
                From: ANSS-netops
                [<a class="moz-txt-link-freetext" href="mailto:anss-netops-bounces@geohazards.usgs.gov">mailto:anss-netops-bounces@geohazards.usgs.gov</a>] On<br>
                Behalf Of Mitchell M Withers (mwithers)<br>
                Sent: Monday, January 05, 2015 7:12 AM<br>
                To: Philip Crotwell<br>
                Cc: <a class="moz-txt-link-abbreviated" href="mailto:anss-netops@geohazards.usgs.gov">anss-netops@geohazards.usgs.gov</a><br>
                Subject: Re: [ANSS-netops] solar power problems<br>
                <br>
                <br>
                Here is a snippet from a recent report from a visit to
                an example station<br>
                with a reftek, three S-13's, and an episensor.  Stations
                vary of course<br>
                and we do use low voltage cutouts at every station
                (fancy ones that cut<br>
                out the transmitter first, then the DAS and everything
                else if the<br>
                voltage<br>
                continues to get lower).<br>
                <br>
                "The new battery banks, when installed were at 12.95 and
                12.98. The total<br>
                station draw is exactly 600ma (checked continuously for
                about three<br>
                minutes). I did a quick calculation of 4 batteries at
                96AH each, 384/.6 =<br>
                640/24 =26.6 days. This calculation would assume no
                solar charge, but<br>
                does<br>
                not take into account reduced battery capacity due to
                cold temperatures."<br>
                <br>
                The panels at that particular station were supplying
                about 700ma together<br>
                on an overcast day and are being replaced with bigger
                panels this week.<br>
                Of course one solution is more battery and more solar at
                every station<br>
                along with more frequent refreshing of batteries.  But
                that gets<br>
                expensive<br>
                and time consuming so I was fishing to see if anyone is
                doing something<br>
                creative. (e.g. wind or hamster wheels).<br>
                <br>
                Mitch<br>
                <br>
                Center for Earthquake Research and Information (CERI)<br>
                University of Memphis                Ph: 901-678-4940<br>
                Memphis, TN 38152                   Fax: 901-678-4734<br>
                <br>
                <br>
                ________________________________________<br>
                From: Philip Crotwell <a class="moz-txt-link-rfc2396E" href="mailto:crotwell@seis.sc.edu"><crotwell@seis.sc.edu></a><br>
                Sent: Monday, January 5, 2015 7:50 AM<br>
                To: Mitchell M Withers (mwithers)<br>
                Cc: <a class="moz-txt-link-abbreviated" href="mailto:anss-netops@geohazards.usgs.gov">anss-netops@geohazards.usgs.gov</a><br>
                Subject: Re: [ANSS-netops] solar power problems<br>
                <br>
                Hi<br>
                <br>
                How did you come up with your 25 day figure? Can you put
                some numbers on<br>
                power input and output?<br>
                <br>
                We use two 105 amp-hour batteries per station, where the
                load is about<br>
                1/2 an amp. That gives me about 17.5 days theoretically,
                but my<br>
                understanding is that you never want to discharge
                batteries anywhere near<br>
                their rating as they can be damaged by high discharges.
                So maybe worry<br>
                less about age and more about installed capacity, ie
                double the battery<br>
                and replace them half as often.<br>
                <br>
                We also, because of the cell modems, can monitor the
                battery voltage over<br>
                time, we have a cron job to ping the cell modem once an
                hour and ask it<br>
                what the input voltage is. For example here is the last
                few days at one<br>
                station. You can definitely tell the difference between
                sunny days and<br>
                rain, and we get a heads up if the power is getting low
                and can do<br>
                something before the station goes down.<br>
<a class="moz-txt-link-freetext" href="http://eeyore.seis.sc.edu/earthworm/status/HAW_last720.png">http://eeyore.seis.sc.edu/earthworm/status/HAW_last720.png</a><br>
                <br>
                Here is another station that we are becoming worried
                about, looks like I<br>
                might get to go on a road trip soon!<br>
<a class="moz-txt-link-freetext" href="http://eeyore.seis.sc.edu/earthworm/status/CASEE_last720.png">http://eeyore.seis.sc.edu/earthworm/status/CASEE_last720.png</a><br>
                <br>
                Philip<br>
                <br>
                On Sun, Jan 4, 2015 at 9:07 AM, Mitchell M Withers
                (mwithers)<br>
                <a class="moz-txt-link-rfc2396E" href="mailto:mwithers@memphis.edu"><mwithers@memphis.edu></a> wrote:<br>
                <blockquote type="cite"><br>
                  Many of our stations run on battery and solar and that
                  normally works<br>
                </blockquote>
                <br>
                well.  We have a routine battery replacement cycle to
                make sure they<br>
                don't<br>
                get old.  Theoretically, we should be able to run with
                zero solar for<br>
                about 25 days.  But this has been an unusually dreary
                winter in the<br>
                southeast and we haven't had much sun for the past two
                months or more.<br>
                I'm wondering what others do in areas with limited
                sunlight to power<br>
                stations that don't have AC available?<br>
                <blockquote type="cite"><br>
                  Mitch<br>
                  <br>
                  Center for Earthquake Research and Information (CERI)<br>
                  University of Memphis                Ph: 901-678-4940<br>
                  Memphis, TN 38152                   Fax: 901-678-4734<br>
                  <br>
                  _______________________________________________<br>
                  ANSS-netops mailing list<br>
                  <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
<a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
                </blockquote>
                <br>
                _______________________________________________<br>
                ANSS-netops mailing list<br>
                <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
                <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
                _______________________________________________<br>
                ANSS-netops mailing list<br>
                <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
                <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
                <br>
              </blockquote>
              <br>
              --<br>
              <br>
============================================================<br>
              <br>
              Robert W. Busby<br>
              Transportable Array Manager           508-801-7628<br>
              USArray / EarthScope                  37 Haynes Avenue<br>
              <a class="moz-txt-link-abbreviated" href="http://www.earthscope.org/usarray">www.earthscope.org/usarray</a>            Falmouth MA USA
              02540-2312<br>
              <br>
              _______________________________________________<br>
              ANSS-netops mailing list<br>
              <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
              <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
            </blockquote>
            <br>
            <br>
            <br>
            <br>
            --<br>
            *********************************************************<br>
            Mark Meremonte         Geophysicist<br>
            U.S. Bureau of Reclamation:  Seismotectonics &
            Geophysics Group<br>
            Denver Federal Center            Work: 303-445-3298  Cell:
            303-808-3894<br>
            POBox 25007, 85-833000      Email: <a class="moz-txt-link-abbreviated" href="mailto:mmeremonte@usbr.gov">mmeremonte@usbr.gov</a><br>
            Denver, CO  80225                  Web: <a class="moz-txt-link-freetext" href="http://www.usbr.gov">http://www.usbr.gov</a><br>
            Ship:  U.S. Bureau of Reclamation, DFC, Bldg. 67-10th Floor,
            Denver, CO<br>
            80225<br>
            **********************************************************<br>
            <br>
            <br>
            _______________________________________________<br>
            ANSS-netops mailing list<br>
            <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
            <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
            <br>
            <br>
            <br>
            _______________________________________________<br>
            ANSS-netops mailing list<br>
            <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
            <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
            <br>
          </blockquote>
          <br>
          <br>
          ------------------------------<br>
          <br>
          Message: 2<br>
          Date: Wed, 7 Jan 2015 12:40:18 -0600<br>
          From: Greg Steiner <a class="moz-txt-link-rfc2396E" href="mailto:vlf@cablerocket.com"><vlf@cablerocket.com></a><br>
          To: <a class="moz-txt-link-rfc2396E" href="mailto:anss-netops@geohazards.usgs.gov"><anss-netops@geohazards.usgs.gov></a><br>
          Subject: Re: [ANSS-netops] ANSS-netops Digest, Vol 59, Issue 6<br>
          Message-ID: <a class="moz-txt-link-rfc2396E" href="mailto:54AD7D92.6020804@cablerocket.com"><54AD7D92.6020804@cablerocket.com></a><br>
          Content-Type: text/plain; charset="windows-1252";
          format=flowed<br>
          <br>
          Patrick, I'm curious as to how you get multiple MPPT
          controllers to <br>
          charge a single battery bank. Are they inherently designed for
          this form <br>
          of parallel operation?<br>
          Greg Steiner<br>
          <br>
          On 1/7/2015 11:16 AM, <a class="moz-txt-link-abbreviated" href="mailto:anss-netops-request@geohazards.usgs.gov">anss-netops-request@geohazards.usgs.gov</a>
          wrote:<br>
          <blockquote type="cite">Send ANSS-netops mailing list
            submissions to<br>
            <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-abbreviated" href="mailto:anss-netops@geohazards.usgs.gov">anss-netops@geohazards.usgs.gov</a><br>
            <br>
            To subscribe or unsubscribe via the World Wide Web, visit<br>
            <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
            or, via email, send a message with subject or body 'help' to<br>
            <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-abbreviated" href="mailto:anss-netops-request@geohazards.usgs.gov">anss-netops-request@geohazards.usgs.gov</a><br>
            <br>
            You can reach the person managing the list at<br>
            <span class="Apple-tab-span" style="white-space:pre"> </span><a class="moz-txt-link-abbreviated" href="mailto:anss-netops-owner@geohazards.usgs.gov">anss-netops-owner@geohazards.usgs.gov</a><br>
            <br>
            When replying, please edit your Subject line so it is more
            specific<br>
            than "Re: Contents of ANSS-netops digest..."<br>
            <br>
            <br>
            Today's Topics:<br>
            <br>
               1. Re: solar power problems (Patrick Bastien)<br>
            <br>
            <br>
----------------------------------------------------------------------<br>
            <br>
            Message: 1<br>
            Date: Wed, 7 Jan 2015 12:18:20 -0500<br>
            From: Patrick Bastien <a class="moz-txt-link-rfc2396E" href="mailto:bastienp@ldeo.columbia.edu"><bastienp@ldeo.columbia.edu></a><br>
            To: <a class="moz-txt-link-rfc2396E" href="mailto:anss-netops@geohazards.usgs.gov"><anss-netops@geohazards.usgs.gov></a><br>
            Subject: Re: [ANSS-netops] solar power problems<br>
            Message-ID: <a class="moz-txt-link-rfc2396E" href="mailto:54AD6A5C.6080608@ldeo.columbia.edu"><54AD6A5C.6080608@ldeo.columbia.edu></a><br>
            Content-Type: text/plain; charset="iso-8859-1";
            Format="flowed"<br>
            <br>
            The Concorde Sun Extender PVX-1040T has a nominal capacity
            of 104AH, so<br>
            312AH for the northern TA stations and 208AH for the
            southern TA stations.<br>
            <br>
            Beginning late last summer, the LCSN has begun to switch
            from older<br>
            PWM-style charge controllers to MPPT charge controllers.
            Although it is<br>
            too soon to say something definite, this is seeming to have
            a larger<br>
            effect on station up-time than just adding more panels or
            batteries.<br>
            Something I am doing that might be considered non-standard
            is wiring<br>
            each solar panel individually to its own small MPPT change
            controller.<br>
            This allows each solar panel to generate the maximum amount
            of power<br>
            regardless of the lighting condition of the other solar
            panels. The<br>
            several MPPT charge controllers then feed a common battery
            bank. I then<br>
            regulate the voltage powering the sensor by using a small
            low-noise DCDC<br>
            converter imbedded inside a cable. The MPPT benefits might
            be magnified<br>
            for the LCSN because of the location of many of our solar
            powered<br>
            stations are in forests or forest-adjacent.<br>
            <br>
            <br>
            Patrick Bastien<br>
            LDEO-LCSN<br>
            <br>
            On 1/7/2015 11:06 AM, Meremonte, Mark wrote:<br>
            <blockquote type="cite">Bob,   May I ask the AH size of AGM
              batteries for an average TA<br>
              station?  Thank you, Mark<br>
              <br>
              On Wed, Jan 7, 2015 at 8:29 AM, Robert Busby
              <<a class="moz-txt-link-abbreviated" href="mailto:busby@iris.edu">busby@iris.edu</a><br>
              <a class="moz-txt-link-rfc2396E" href="mailto:busby@iris.edu"><mailto:busby@iris.edu></a>> wrote:<br>
              <br>
                  Hi Mitch et al.<br>
                  This is a good discussion of Power for seismic
              stations, thanks.<br>
              <br>
                  In the Transportable Array deployment, all 1717
              stations<br>
                  operate(d) off solar power for at east two years.  The
              average<br>
                  current draw for a station is 0.5Amps on a 12V system,
              but can<br>
                  vary from 0.4 to 0.6A depending on the telemetry
              system. High<br>
                  current telemetry systems such as VSAT are powered
              separately.  We<br>
                  avoided AC power because of the proximity of noise due
              to pumps,<br>
                  motors, etc.<br>
              <br>
                  In general we use (2) 90W PV panels and (2) AGM Lead
              Acid<br>
                  batteries for stations south of the Kentucky/Tennessee
              line (row U<br>
                  in TA station codes) and (3) 90W PV panels and (3) AGM
              Lead Acid<br>
                  batteris north of there. Shady or snowy sites
              occasionally got<br>
                  more panels and batteries.  For permanent stations I'd
              go with the<br>
                  (3) PV and 3 or 4 batteries.  We prefer good quality
              batteries<br>
                  designed for solar applications, such as the Concorde
              Sun Extender<br>
                  PVX-1040T. We use PWM regulators with Low voltage
              disconnect at<br>
                  10.8V.  A few more sophisticated options are discussed
              below.<br>
              <br>
                  I would concur with the notion that the most effective
              way to<br>
                  improve a marginal station power situation is to add 1
              or 2<br>
                  batteries, and often this can be done without much
              infrastructure<br>
                  alteration. And the next  option is to add a panel.
               There is<br>
                  little concern about over driving the charge
              controller with too<br>
                  much current from too many panels.  In Alaska, the
              "more<br>
                  batteries" approach is taken to extremes in which
              stations have 24<br>
                  batteries to float through the winter. I would also
              concur that,<br>
                  to date, neither wind nor fuel cells have proved
              reliable enough<br>
                  to warrant their use, especially in permanent stations
              of the Lower48.<br>
              <br>
                  More complexity described below:<br>
                  Our system has, in addition to the main battery bank,
              a small<br>
                  reserve battery.  When the system switches to the
              reserve, certain<br>
                  loads such as the telemetry radio and local data
              storage are duty<br>
                  cycled at four hour intervals.  This reduces the power
              of the<br>
                  station to about 3W, yet still provides complete
              telemetry (though<br>
                  with episodic latency) and complete local storage.
               For us, this<br>
                  reserve power serves to identify the source of the
              outage is<br>
                  clearly power as opposed to a host of other
              possibilities.  In the<br>
                  original design this reserve battery was Alkaline
              Lattern 30AH<br>
                  batteries [(3) x 6Volts] (a primary battery, disposed
              of after<br>
                  use).  More recently, We have also used 100-300AH
              rechargeable<br>
                  batteries that are then connected to the main
              batteries using a<br>
                  battery isolator circuit-which connects the reserve
              batteries to<br>
                  the charger only when the main battery has recharged
              to 13.2V.  We<br>
                  add a 10A current limit to the battery
              interconnection.  The<br>
                  reserve power load shedding  can be thought of as
              doubling the<br>
                  capacity of the reserve batteries, reducing the cost
              of overall<br>
                  power system for this reserve capability.  Without
              that<br>
                  sophisitication of load shedding, adding more
              batteries is<br>
                  effective but there is a cost in terms of station
              uptime. When a<br>
                  very large, undifferentiated battery bank is depleted,
              it will<br>
                  take a longer time for the batteries to reach the
              reconnect<br>
                  voltage.  In this time, the station itself could be
              operating on<br>
                  the minimal power produced. We keep the main battery
              bank fairly<br>
                  modest so it recovers voltage quickly, and defer
              recharging the<br>
                  reserve pack until there is ample power-sometimes
              weeks, or in<br>
                  Alaska, months later.  Its meant to get you through an
              ocasional<br>
                  bad spell.  One issue in this reserve battery
              switching is the dc<br>
                  currents can introduce magnetic pulses seen on the<br>
                  seismometer-particularly Trilliums within a few meters
              of the<br>
                  switches.<br>
              <br>
                  If you are plannning a Net-ops meeting in the future,
              I'd be<br>
                  happly to elaborate on the power system for Alaska,
              which uses a<br>
                  Genasun MPPT charge controller and LiFePO4 (Lithium
              Ion) batteries<br>
                  and the same duty cycle loads, reserve battery
              concepts.  These<br>
                  significantly reduce the weight of a 1440AH system to
              420 lbs and<br>
                  do not require derating the capacity for cold
              temperatures.  They<br>
                  are very expensive, but not as much as a helicopter
              trip.<br>
              <br>
                  Bob Busby<br>
                  TA Manager<br>
              <br>
                  On 1/6/2015 7:36 AM, Kyle Persefield wrote:<br>
              <br>
                      Mitch,<br>
              <br>
                      My 2 cents worth<br>
              <br>
                      Because of cost, we have found throwing on more
              solar panels<br>
                      to be the<br>
                      cheapest and least maintenance intensive solution.
               Fuel cells and<br>
                      thermoelectric generators are expensive and then
              there is the<br>
                      recurring<br>
                      cost for fuel, getting fuel to the site, then
              monitoring of<br>
                      the fuel<br>
                      supply level to consider, and the added required
              maintenance.<br>
                      We have not<br>
                      found a solution to use these devices as demand
              requires their<br>
                      use.  Or<br>
                      turning them on and off as needed.  So long as
              there is fuel<br>
                      they are on.<br>
              <br>
                      We have been very disappointed with wind turbines.
               The<br>
                      smaller ones,<br>
                      which are designed for the consumer market, the
              bearings<br>
                      always fail.<br>
                      Expect no more than 2 or3 years out of these
              "cheap" units.<br>
                      Then of<br>
                      course there is the need for wind.  No wind for
              extended<br>
                      periods is just<br>
                      as bad as your overcast scenario.<br>
              <br>
                      Kyle<br>
              <br>
                      -----Original Message-----<br>
                      From: ANSS-netops<br>
                      [<a class="moz-txt-link-freetext" href="mailto:anss-netops-bounces@geohazards.usgs.gov">mailto:anss-netops-bounces@geohazards.usgs.gov</a><br>
                      <a class="moz-txt-link-rfc2396E" href="mailto:anss-netops-bounces@geohazards.usgs.gov"><mailto:anss-netops-bounces@geohazards.usgs.gov></a>]
              On<br>
                      Behalf Of Mitchell M Withers (mwithers)<br>
                      Sent: Monday, January 05, 2015 7:12 AM<br>
                      To: Philip Crotwell<br>
                      Cc: <a class="moz-txt-link-abbreviated" href="mailto:anss-netops@geohazards.usgs.gov">anss-netops@geohazards.usgs.gov</a><br>
                      <a class="moz-txt-link-rfc2396E" href="mailto:anss-netops@geohazards.usgs.gov"><mailto:anss-netops@geohazards.usgs.gov></a><br>
                      Subject: Re: [ANSS-netops] solar power problems<br>
              <br>
              <br>
                      Here is a snippet from a recent report from a
              visit to an<br>
                      example station<br>
                      with a reftek, three S-13's, and an episensor.
               Stations vary<br>
                      of course<br>
                      and we do use low voltage cutouts at every station
              (fancy ones<br>
                      that cut<br>
                      out the transmitter first, then the DAS and
              everything else if<br>
                      the voltage<br>
                      continues to get lower).<br>
              <br>
                      "The new battery banks, when installed were at
              12.95 and<br>
                      12.98. The total<br>
                      station draw is exactly 600ma (checked
              continuously for about<br>
                      three<br>
                      minutes). I did a quick calculation of 4 batteries
              at 96AH<br>
                      each, 384/.6 =<br>
                      640/24 =26.6 days. This calculation would assume
              no solar<br>
                      charge, but does<br>
                      not take into account reduced battery capacity due
              to cold<br>
                      temperatures."<br>
              <br>
                      The panels at that particular station were
              supplying about<br>
                      700ma together<br>
                      on an overcast day and are being replaced with
              bigger panels<br>
                      this week.<br>
                      Of course one solution is more battery and more
              solar at every<br>
                      station<br>
                      along with more frequent refreshing of batteries.
               But that<br>
                      gets expensive<br>
                      and time consuming so I was fishing to see if
              anyone is doing<br>
                      something<br>
                      creative. (e.g. wind or hamster wheels).<br>
              <br>
                      Mitch<br>
              <br>
                      Center for Earthquake Research and Information
              (CERI)<br>
                      University of Memphis                Ph:
              901-678-4940<br>
                      Memphis, TN 38152                   Fax:
              901-678-4734<br>
              <br>
              <br>
                      ________________________________________<br>
                      From: Philip Crotwell <<a class="moz-txt-link-abbreviated" href="mailto:crotwell@seis.sc.edu">crotwell@seis.sc.edu</a><br>
                      <a class="moz-txt-link-rfc2396E" href="mailto:crotwell@seis.sc.edu"><mailto:crotwell@seis.sc.edu></a>><br>
                      Sent: Monday, January 5, 2015 7:50 AM<br>
                      To: Mitchell M Withers (mwithers)<br>
                      Cc: <a class="moz-txt-link-abbreviated" href="mailto:anss-netops@geohazards.usgs.gov">anss-netops@geohazards.usgs.gov</a><br>
                      <a class="moz-txt-link-rfc2396E" href="mailto:anss-netops@geohazards.usgs.gov"><mailto:anss-netops@geohazards.usgs.gov></a><br>
                      Subject: Re: [ANSS-netops] solar power problems<br>
              <br>
                      Hi<br>
              <br>
                      How did you come up with your 25 day figure? Can
              you put some<br>
                      numbers on<br>
                      power input and output?<br>
              <br>
                      We use two 105 amp-hour batteries per station,
              where the load<br>
                      is about<br>
                      1/2 an amp. That gives me about 17.5 days
              theoretically, but my<br>
                      understanding is that you never want to discharge
              batteries<br>
                      anywhere near<br>
                      their rating as they can be damaged by high
              discharges. So<br>
                      maybe worry<br>
                      less about age and more about installed capacity,
              ie double<br>
                      the battery<br>
                      and replace them half as often.<br>
              <br>
                      We also, because of the cell modems, can monitor
              the battery<br>
                      voltage over<br>
                      time, we have a cron job to ping the cell modem
              once an hour<br>
                      and ask it<br>
                      what the input voltage is. For example here is the
              last few<br>
                      days at one<br>
                      station. You can definitely tell the difference
              between sunny<br>
                      days and<br>
                      rain, and we get a heads up if the power is
              getting low and can do<br>
                      something before the station goes down.<br>
        <a class="moz-txt-link-freetext" href="http://eeyore.seis.sc.edu/earthworm/status/HAW_last720.png">http://eeyore.seis.sc.edu/earthworm/status/HAW_last720.png</a><br>
              <br>
                      Here is another station that we are becoming
              worried about,<br>
                      looks like I<br>
                      might get to go on a road trip soon!<br>
        <a class="moz-txt-link-freetext" href="http://eeyore.seis.sc.edu/earthworm/status/CASEE_last720.png">http://eeyore.seis.sc.edu/earthworm/status/CASEE_last720.png</a><br>
              <br>
                      Philip<br>
              <br>
                      On Sun, Jan 4, 2015 at 9:07 AM, Mitchell M Withers
              (mwithers)<br>
                      <<a class="moz-txt-link-abbreviated" href="mailto:mwithers@memphis.edu">mwithers@memphis.edu</a>
              <a class="moz-txt-link-rfc2396E" href="mailto:mwithers@memphis.edu"><mailto:mwithers@memphis.edu></a>> wrote:<br>
              <br>
                          Many of our stations run on battery and solar
              and that<br>
                          normally works<br>
              <br>
                      well.  We have a routine battery replacement cycle
              to make<br>
                      sure they don't<br>
                      get old.  Theoretically, we should be able to run
              with zero<br>
                      solar for<br>
                      about 25 days.  But this has been an unusually
              dreary winter<br>
                      in the<br>
                      southeast and we haven't had much sun for the past
              two months<br>
                      or more.<br>
                      I'm wondering what others do in areas with limited
              sunlight to<br>
                      power<br>
                      stations that don't have AC available?<br>
              <br>
                          Mitch<br>
              <br>
                          Center for Earthquake Research and Information
              (CERI)<br>
                          University of Memphis                Ph:
              901-678-4940<br>
                          Memphis, TN 38152                   Fax:
              901-678-4734<br>
              <br>
            _______________________________________________<br>
                          ANSS-netops mailing list<br>
                          <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
                          <a class="moz-txt-link-rfc2396E" href="mailto:ANSS-netops@geohazards.usgs.gov"><mailto:ANSS-netops@geohazards.usgs.gov></a><br>
            <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
              <br>
                      _______________________________________________<br>
                      ANSS-netops mailing list<br>
                      <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
                      <a class="moz-txt-link-rfc2396E" href="mailto:ANSS-netops@geohazards.usgs.gov"><mailto:ANSS-netops@geohazards.usgs.gov></a><br>
        <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
                      _______________________________________________<br>
                      ANSS-netops mailing list<br>
                      <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
                      <a class="moz-txt-link-rfc2396E" href="mailto:ANSS-netops@geohazards.usgs.gov"><mailto:ANSS-netops@geohazards.usgs.gov></a><br>
        <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
              <br>
              <br>
                  --<br>
              <br>
    ============================================================<br>
              <br>
                  Robert W. Busby<br>
                  Transportable Array Manager           508-801-7628<br>
                  USArray / EarthScope                  37 Haynes Avenue<br>
                  <a class="moz-txt-link-abbreviated" href="http://www.earthscope.org/usarray">www.earthscope.org/usarray</a>
              <a class="moz-txt-link-rfc2396E" href="http://www.earthscope.org/usarray"><http://www.earthscope.org/usarray></a><br>
                        Falmouth MA USA 02540-2312<br>
              <br>
                  _______________________________________________<br>
                  ANSS-netops mailing list<br>
                  <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
                  <a class="moz-txt-link-rfc2396E" href="mailto:ANSS-netops@geohazards.usgs.gov"><mailto:ANSS-netops@geohazards.usgs.gov></a><br>
    <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
              <br>
              <br>
              <br>
              <br>
              --<br>
              *********************************************************<br>
              Mark Meremonte         Geophysicist<br>
              U.S. Bureau of Reclamation:  Seismotectonics &
              Geophysics Group<br>
              Denver Federal Center            Work: 303-445-3298  Cell:
              303-808-3894<br>
              POBox 25007, 85-833000Email: <a class="moz-txt-link-abbreviated" href="mailto:mmeremonte@usbr.gov">mmeremonte@usbr.gov</a><br>
              <a class="moz-txt-link-rfc2396E" href="mailto:mmeremonte@usbr.gov"><mailto:mmeremonte@usbr.gov></a><br>
              Denver, CO  80225     Web: <a class="moz-txt-link-freetext" href="http://www.usbr.gov">http://www.usbr.gov</a><br>
              Ship: U.S. Bureau of Reclamation, DFC, Bldg. 67-10th
              Floor, Denver, CO<br>
              80225<br>
              **********************************************************<br>
              <br>
              <br>
              _______________________________________________<br>
              ANSS-netops mailing list<br>
              <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
              <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
            </blockquote>
            <br>
            -------------- next part --------------<br>
            An HTML attachment was scrubbed...<br>
            URL:
<a class="moz-txt-link-rfc2396E" href="http://geohazards.usgs.gov/pipermail/anss-netops/attachments/20150107/ccb8aea5/attachment.html"><http://geohazards.usgs.gov/pipermail/anss-netops/attachments/20150107/ccb8aea5/attachment.html></a><br>
            <br>
            ------------------------------<br>
            <br>
            Subject: Digest Footer<br>
            <br>
            _______________________________________________<br>
            ANSS-netops mailing list<br>
            <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
            <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
            <br>
            <br>
            ------------------------------<br>
            <br>
            End of ANSS-netops Digest, Vol 59, Issue 6<br>
            ******************************************<br>
            <br>
          </blockquote>
          <br>
          <br>
          ------------------------------<br>
          <br>
          Subject: Digest Footer<br>
          <br>
          _______________________________________________<br>
          ANSS-netops mailing list<br>
          <a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a><br>
          <a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a><br>
          <br>
          <br>
          ------------------------------<br>
          <br>
          End of ANSS-netops Digest, Vol 59, Issue 7<br>
          ******************************************<br>
        </blockquote>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
ANSS-netops mailing list
<a class="moz-txt-link-abbreviated" href="mailto:ANSS-netops@geohazards.usgs.gov">ANSS-netops@geohazards.usgs.gov</a>
<a class="moz-txt-link-freetext" href="https://geohazards.usgs.gov/mailman/listinfo/anss-netops">https://geohazards.usgs.gov/mailman/listinfo/anss-netops</a>
</pre>
    </blockquote>
    <br>
    <div class="moz-signature">-- <br>
      <pre>============================================================

Robert W. Busby
Transportable Array Manager           508-801-7628
USArray / EarthScope                  37 Haynes Avenue
<a class="moz-txt-link-abbreviated" href="http://www.earthscope.org/usarray">www.earthscope.org/usarray</a>            Falmouth MA USA 02540-2312
</pre>
    </div>
  </body>
</html>